• We’re currently investigating an issue related to the forum theme and styling that is impacting page layout and visual formatting. The problem has been identified, and we are actively working on a resolution. There is no impact to user data or functionality, this is strictly a front-end display issue. We’ll post an update once the fix has been deployed. Thanks for your patience while we get this sorted.

Need device to monitor/report electrical usage based on KW/hour

Status
Not open for further replies.
Hi Guys,

I have to find a device that would be installed during a new circuit installation in our datacenter. It would need to be installed in front of a circuit so it would display the power usage based on kw/hour.

Typically, we simply provide a full 20amp/120volt circuit (or other type if needed) and we charge a flat rate for the circuit. Our price is based on 80% utilization. Typically, it is $250 per month per 120volt/20amp circuit. Keep in mind, this is redundant, clean, power with both battery backup and generator backup.

We have one potential customer that needs close to 12 20amp/208v circuits. However, they only plan to use 12-18% of each circuit's capacity, and it is going to fluctuate. They are getting bids from competitors to simply bill them according to actual usage, not on a flat rate per circuit.

I have to pitch to my boss today before 5pm how we would modify our billing to accomodate the client. I need to be able to show him a device, not specifically the exact one we would use, but as an example, what could be installed to report actual usage. The client is willing to buy the devices.

Any ideas? I'm checking out APC and Schneider Elec now.. but not quite finding anything yet.
 
Just get a network enabled PDU for the racks and use SNMP to monitor them and build graphs for utilization.
 
Are all their circuits in one place ? ?
Easiest way is install a feed from your main electric panel to a Utility Meter (same as the power co uses) and then from that to a sub panel. Run their branch circuits off that panel to where they need them. You do
not need to meter each individual circuit, just the feed to them. Any electrician can easily do this job.
 
Any major electrical supplier will supply 'energy meters' of various sophistication - up to and including high-precision 3-phase meters with minute by minute logging and ethernet communications for downloading data.

However, lower-cost simple meters are readily available:
e.g. Schneider electric EN40. These mini-meters simply slot into a standard electrical panel - each meter takes up 2 breaker slots, allowing you to install up to 12 meters in one panel. (Just a note, I don't know how US electric friendly these Schneider meters are, being a French company and all).

You are best off contacting an electrical supplier to see what they can offer - this type of thing is pretty standard.
 
Are all their circuits in one place ? ?
Easiest way is install a feed from your main electric panel to a Utility Meter (same as the power co uses) and then from that to a sub panel. Run their branch circuits off that panel to where they need them. You do
not need to meter each individual circuit, just the feed to them. Any electrician can easily do this job.
This.
Sub panel with a meter. Any competant Electrical contractor can do this.
 
This.
Sub panel with a meter. Any competant Electrical contractor can do this.

yup.. that's what we are doing.

the whole issue was that they needed a lot of circuits.. but were going to barely use them.

Regardless of how much they use, we still have to plan for their total capacity.

So if we provide them 200amps of capacity, and they only plan to use 20amps, we still need to consider the 200amps of potential usage there.

So we are going to install subpanels that can be capped and metered.
 
Status
Not open for further replies.
Back
Top