Furnace turns on every 10 minutes

Discussion in 'Off Topic' started by Triumph, Feb 12, 2012.

  1. Triumph

    Triumph Lifer

    Joined:
    Oct 9, 1999
    Messages:
    14,986
    Likes Received:
    1
    I'm a new(ish) homeowner so I never noticed such things before, but I installed a thermostat, a Honeywell from HD that ran about $60, and the thing turns the furnace on about every 10 minutes and runs it for 7-8 minutes. With my old thermostat, I don't remember it ever operating this frequently. I looked in the manual, there's no option to adjust how sensitive it is (i.e. how much the temperature has to drop before it will turn on). I changed the thermostat in the first place to get the weekday and weekend scheduling options, not sure if that actually saves any money. Seems to me it'd be more efficient to try and keep at a constant temperature rather than losing all that heat during the day and trying to make it up in the evening.
     
  2. Red Squirrel

    Red Squirrel Lifer

    Joined:
    May 24, 2003
    Messages:
    36,965
    Likes Received:
    635
    The span time is probably too low, so it's short cycling. Is it doing it more when it's really cold? I'm not familiar with that thermostat but see if there's an option called "span", though it may be called something else.

    I've been working on a fully custom thermostat, and I'm actually going to set the temp in ranges. It cost less money to run the furnace for a long time, then to run it in a bunch of short cycles so the idea will be to avoid short cycling as much as possible.

    Though if you have high heat loss it's harder to avoid.
     
  3. FoBoT

    FoBoT No Lifer

    Joined:
    Apr 30, 2001
    Messages:
    63,089
    Likes Received:
    0
    what kind of 'furnace' is it?
     
  4. bruceb

    bruceb Diamond Member

    Joined:
    Aug 20, 2004
    Messages:
    7,868
    Likes Received:
    3
    We need to know the type of furnace. Oil or Gas fired, hot water baseboard heat or hot air heat. All that makes a difference in how the thermostat options are set up. We also need the exact model of the thermostat that you bought from Home Depot. There are usually a few screw terminals on them and depending on the furnace, you may need to jumper a couple of them or there may be a screw that sets the amount of "on time" before it will go off or come back on again. For example, in a hot air system the fan will stay on a couple of minutes after the furnace goes off.
     
  5. Triumph

    Triumph Lifer

    Joined:
    Oct 9, 1999
    Messages:
    14,986
    Likes Received:
    1
    Brand I don't remember, but I am in a ~1500 sq ft townhouse in Virginia and it is a gas furnace with electric blower. Today is about 30 degrees outside.
     
  6. Analog

    Analog Lifer

    Joined:
    Jan 7, 2002
    Messages:
    12,755
    Likes Received:
    0
    Sounds like the hysteresis is set to tight. Your older T-stat must have had a wider hysteresis setting. I'm not sure if you are able to change that on the new one.
     
  7. Red Squirrel

    Red Squirrel Lifer

    Joined:
    May 24, 2003
    Messages:
    36,965
    Likes Received:
    635
    30 degrees F? Yeah the furnace should not be running that often. I could see that when it's like -20 or so. When it stops, is it at the temp you set it at though? If yes, then you could also have major heat loss going on, maybe not enough insulation in the attic.
     
  8. Triumph

    Triumph Lifer

    Joined:
    Oct 9, 1999
    Messages:
    14,986
    Likes Received:
    1
    I don't think I can. It is a Honeywell RTH6450. The only thing that comes close in the manual is a "heating cycle rate," which only has the following options:
    Set to 5 if you have gas or oil furnace
    Set to 9 if you have electric furnace
    Set to 3 if you have hot water or high efficiency furnace
    Set to 1 if you have gas/oil steam or gravity system

    So mine is obviously set to 5. There is nothing else in the manual that I can see that would change this.
     
  9. Analog

    Analog Lifer

    Joined:
    Jan 7, 2002
    Messages:
    12,755
    Likes Received:
    0
    I don't know about yours, but some have set-screw adjustments on the back side for such things.
     
  10. JEDI

    JEDI Lifer

    Joined:
    Sep 25, 2001
    Messages:
    23,192
    Likes Received:
    6
    my lux programmable thermostat says my system should cycle 3 to 6 times per hour.

    so every 10min sounds like its within range.
     
  11. Triumph

    Triumph Lifer

    Joined:
    Oct 9, 1999
    Messages:
    14,986
    Likes Received:
    1
    I turned the heat off after the last cycle, and it took about 25 minutes to drop 1 degree. Granted it is getting warmer outside but I figure this is a good enough test of my insulation (which I know I have problems in the entry hall). I would prefer to adjust this thermostat so that it turned on after dropping 1 degree instead of 1/10th of a degree or whatever it's set to. There's nothing in the manual nor a screw adjustment on the module anywhere that speaks to adjusting this sensitivity.

    Anyone have a suggestion for a good thermostat?

    Thanks for that, that's good feedback.
     
  12. arcenite

    arcenite Lifer

    Joined:
    Dec 9, 2001
    Messages:
    10,642
    Likes Received:
    0
    I believe the heating cycling rate is exactly what you should be looking at. Change it to 3 and see if there's any improvement.
     
  13. Thump553

    Thump553 Diamond Member

    Joined:
    Jun 2, 2000
    Messages:
    9,930
    Likes Received:
    6
    That's a perfectly good thermostat-I have two of them in central CT and both run perfectly.

    Check to see if all the bottom switches are set correctly, then I'd follow Jedi's suggestions and if that doesn't work, call the Honeywell hotline-they are very helpful.
     
  14. Engineer

    Engineer Elite Member

    Joined:
    Oct 9, 1999
    Messages:
    37,909
    Likes Received:
    3
    This. Most of the programmable thermostats that I've seen have a 1,2 or 3 degree hysteresis.

    OT: My new system simply keeps the temperature where it's set by varying the blower speed up/down like a servo system. Most consistent (and cheap - 95.5% efficient) furnace I've ever had.
     
  15. JEDI

    JEDI Lifer

    Joined:
    Sep 25, 2001
    Messages:
    23,192
    Likes Received:
    6
    why 3?

    changing from 5 to 3 will increase sensitivity, thus more cycles?
     
  16. Rubycon

    Rubycon Madame President

    Joined:
    Aug 10, 2005
    Messages:
    17,289
    Likes Received:
    127
    How many btu/hr is the furnace?
    Where is the thermostat located? Usually it's in a hallway away from drafts from doors and located near a return. Digital stats are far more sensitive than aneroid bi-metal old school stats like T87F etc.
    Does it have an anticipator?
     
  17. waggy

    waggy No Lifer

    Joined:
    Dec 14, 2000
    Messages:
    68,161
    Likes Received:
    5
    ohh im going to piggyback on this thread (sorry op). but I think my thermostat is going (only after 7 years!) it keeps letting the temp drop. the other day it got to 61.

    i had it set to 74 during the day and 69 at night. I had to set ot override and to 74 only room that is cool is the office/playroom (haven't got new windows in this room yet)
     
  18. bruceb

    bruceb Diamond Member

    Joined:
    Aug 20, 2004
    Messages:
    7,868
    Likes Received:
    3
    Recheck your settings. Also the type of heating system (hot water baseboard or hot air) and wether it is a newer high efficiency furnace will have to use the correct settings.

    Set to 5 if you have gas or oil furnace ... this would be for normal, old hot air furnace
    Set to 9 if you have electric furnace .. not many homes have this type
    Set to 3 if you have hot water or high efficiency furnace .. hot water baseboard heat or new high efficiency furnace
    Set to 1 if you have gas/oil steam or gravity system ... only used if you have steam radiators found in many very older homes

    Note you can check the nameplate on the furnace. If it is within say 4 years or so old and has a rating of 80% or higher, it is a high efficiency type of unit.
     
  19. arcenite

    arcenite Lifer

    Joined:
    Dec 9, 2001
    Messages:
    10,642
    Likes Received:
    0
    It has nothing to do with sensitivity to temperature.

    The lower the number the less times per hour the system will kick on and off.

    5 = 60/5 = Tstat cycles a maximum of once every 12 mins
    3 = 60/3 = Tstat cycles a maximum of once every 20 mins

    That's my understanding anyway.
     
    #19 arcenite, Feb 12, 2012
    Last edited: Feb 12, 2012
  20. iGas

    iGas Diamond Member

    Joined:
    Feb 7, 2009
    Messages:
    6,240
    Likes Received:
    0
    Second the hysteresis theory.
     
  21. Triumph

    Triumph Lifer

    Joined:
    Oct 9, 1999
    Messages:
    14,986
    Likes Received:
    1
    It is a 20 year old Rheem unit. I had the AC serviced last summer and the heat checked out in the fall. It works good, the HVAC guy said it was one of his favorite units and to run it until it dies. Which I plan on doing. So the #5 setting is correct for it.

    Even though the #5 setting is technically correct for me, I will try setting it to 3 and see what happens. I don't like this unit, the manual should make some explanation of what this setting is, without you and I having to guess at it.
     
  22. ElFenix

    ElFenix Elite Member<br> Super Moderator<br>Off Topic
    Super Moderator

    Joined:
    Mar 20, 2000
    Messages:
    95,967
    Likes Received:
    61
    it's not.
     
  23. yh125d

    yh125d Diamond Member

    Joined:
    Dec 23, 2006
    Messages:
    6,918
    Likes Received:
    0
    Yeah, in fact that's pretty much the sole reason programmable timer t-stats were invented.
     
  24. DrPizza

    DrPizza Administrator Elite Member Goat Whisperer
    Administrator

    Joined:
    Mar 5, 2001
    Messages:
    49,629
    Likes Received:
    153
    To answer your other question, yes, it saves energy. Your house loses energy at a rate proportional to the difference in temperature between indoors and outside.
     
  25. LiuKangBakinPie

    LiuKangBakinPie Diamond Member

    Joined:
    Jan 31, 2011
    Messages:
    3,912
    Likes Received:
    0
    I can honestly say that everyone I have sex with always smokes after!

    Then again I am the furnace operator at the crematorium.