For what it's worth, I posted in one of the Reddit threads to shed some light on what I think happened.
/tldr; the construction workers caused the bridge to fail when they prestressed some of the diagonal members on the bridge. Whether or not the engineer or contractor is liable depends on what instructions where given to prestress the diagonal members.
---
Professional Civil Engineer working in structural engineering here (legally can't call myself a Structural Engineer as I have yet to obtain my license), but figured I clear up some potential confusion and weigh in on a possible cause of failure here:
1) The media seems to have heard the word "stressing" and ran with the notion that the construction crew was "stress testing" the bridge. I personally do not design bridges - I design buildings - but one that you do NOT do is "stress test" a structure while it is open to the public. Any testing of structural components should be performed in a lab or in a closed off area such that if something were to fail, it poses no immediate danger to anyone. In other words, this was not a stress test. The media simply misheard, which is understandable given that they are not engineers. What was really happening is that the construction crew was applying prestress to one of the bridge members. According to Marco Rubio's tweet, some of the prestress tendons' anchorage was loose during construction or transportation and there were orders from the lead engineer to tighten the tendons, presumably to get them back up to their design prestress value. Nothing fishy so far about this.
If you look at the security cam footage of the bridge right before collapse, what you see are the construction crew standing right on top of the bridge with their hydraulic jacking equipment ready to tension the loosened tendon. heck, even one of the dudes in the video quips about how one of the crew got hang time as the bridge collapses.
Normally, for a concrete bridge to fail in flexure, i.e. it fails under bending load, the top chord fails in compression load (i.e. it buckles or crushes) or the bottom chord fails in tension (i.e. the rebar/prestress tendons gave out). Where does the point of maximum flexure occur for a simply-supported bridge like this one? Right at mid-span. The failure did not occur at mid-span for this bridge, which suggests the cause of failure was not due to the prestress tendons giving out along the bottom chord.
If you watch closely, you can see that the failure point of the bridge is right directly under where the crew is standing. Note that their position with respect to the length of the bridge; they are standing at the first intersection of the diagonal brace members of the bridge, not at mid-span. Given that the bridge stood up under its own weight earlier in the day, this seems to suggest that the failure mechanism was related to the work the crew was doing.
Rubio's Tweet:
https://twitter.com/marcorubio/status/974486176336957440
2) So what was the construction crew doing exactly? They were prestressing the tendons for the diagonal brace members in the bridge (not the tendons in the top and bottom deck).
Some background info: the role of these diagonal braces (i.e. the truss members) is critical to the structural load carrying capacity of the bridge. To use an analogy, treat this bridge as an I-beam. What makes an I-beam strong and stiff is the fact that its shape allows you to have a deep (i.e. tall) cross section where a lot of the material is at the top most and bottom most part of the section. This results in a section with a high area moment of inertia. Note that intuitively, this only works if you still have some material connecting the top and bottom parts of the beam, resulting in a shape that lends the name "I-beam". Without the strip of material (known as the "web") connecting the top and bottom parts of the beam (called the "chords"), the overall section cannot act as a deeper section and it loses most of its stiffness.
How an I-beam works:
https://www.quora.com/Why-is-an-I-b...l-design-come-to-fulfill-its-primary-function
Now, going back to the pedestrian bridge, the diagonal braces are the web and the top and bottom deck are the chords of the "I-beam".
For those who have taken some form of physics or statics class will have some experience designing a spaghetti truss bridge of some sort during their schooling. They know that the diagonal brace that sees the most compression load are the ones at the far extremes of the span. Yes, the exact same one that were below the construction workers. If this brace (or any brace, really) were to fail, the bridge cannot as as an I-beam at the point where the brace failed and it thus loses most of its strength and collapses. Recall that the bridge failed right under the construction workers...
3) Okay, so if the hypothesis is that one of the diagonal braces failed, which one failed? Good question.
It so happens that there's a 2015 version of the design proposal for the bridge floating around the internet:
https://facilities.fiu.edu/projects/BT_904/MCM_FIGG_Proposal_for_FIU_Pedestrian_Bridge_9-30-2015.pdf
If you go to page 115, one sees the elevation of the bridge. The span on the left (left of the Pylon) is what collapsed. The span on the right was not put in place yet. So, if we focus just on the left span, the failure occurred right where Member 10 and 11 meet. If you look at the table for PT Bar Requirements (PT = "Pre-tensioning" i.e. prestressing), Member 10 is prestressed while Member 11 is not. This makes sense because you typically prestress concrete when you want it to withstand tension loads. Prestressing a member that is expected to take compression loads will only add more compression load to it.
So which diagonal was the construction crew prestressing? From pictures, it appears that it was Member 11, the one that is supposed to take compression loads. One can spot the hydraulic jack that applies the prestress to the tendon by the teal cylinder. It appears that the jack is oriented in a rather flat orientation (i.e. it's almost horizontal). Between Member 10 and 11, the brace that is more horizontal is Member 11, not Member 10.
Pic:
https://res.cloudinary.com/engineering-com/image/upload/v1521183436/tips/MIAMI_3_i7ildl.png
Now, concrete is pretty strong in compression and it takes a lot of compressive force to crush concrete. However, applying compressive force on Member 11 results in Member 10 seeing more tension load, which concrete does not handle well. Recall, Member 10 has prestress tendons for this reason.
Where the mistake could have occurred is anyone's guess but it might boil down to one or more of the following:
- Too much prestress was applied to Member 11, causing Member 11 to fail in compression.
- Too much prestress was applied to Member 11, causing Member 10 and its prestressing tendons to fail in tension.
- The workers accidentally released all prestress in the tendons in Member 11 while prestressing Member 11, causing Member 11 to fail in tension.
- The workers were actually prestressing Member 10 (not 11), and by applying too much prestress, it causes Member 10 to go from resisting tension to resisting compression loads, thus effectively negating it's function as a web member in the "I-beam" and causing the bridge to fail.
4) I'd like to add that the design proposal from 2015 is NOT the final construction documents used to construct the bridge. All information presented in the proposal was subject to change in the final design. Member 11 likely had prestress tendons specified for it in the final construction documents, which means that the construction workers were correct in prestressing Member 11 (assuming they were indeed prestressing Member 11, of course).
Thus, without more information, the crux of the hypothesis remains is as follows: the act of "tightening" the prestressing Member 11 caused either Member 10 or Member 11 to fail, thus taking out the bridge with it.
For more information, you can follow this thread:
http://www.eng-tips.com/viewthread.cfm?qid=436595
The engineers there have essentially laid out the arguments I presented above and credit is due to them for fleshing out some of the finer details presented.