So obviously I have multiple servers with redundent power supplies and about 6 UPSs. Which is the proper setup?
 

Zim Hosein

Super Moderator | Elite Member
Super Moderator
Nov 27, 1999
65,512
408
126
Each power supply into a separate power strip, and then into different UPS &
I don't know much, but I know I love you, and that may be all I need to know

:p
 

ThisIsMatt

Banned
Aug 4, 2000
11,820
1
0
How are the first two really any different? Are your power strips not capable of handling the load of two power supplies?
 

Zim Hosein

Super Moderator | Elite Member
Super Moderator
Nov 27, 1999
65,512
408
126
Originally posted by: ThisIsMatt
How are the first two really any different? Are your power strips not capable of handling the load of two power supplies?

Separate powers strips provide another layer of protection.
 

TheNinja

Lifer
Jan 22, 2003
12,207
1
0
Originally posted by: ThisIsMatt
How are the first two really any different? Are your power strips not capable of handling the load of two power supplies?

I guess the first two are pretty close to the same, but like Zim mentioned, it technically adds another layer.
 

ThisIsMatt

Banned
Aug 4, 2000
11,820
1
0
Originally posted by: Zim Hosein
Originally posted by: ThisIsMatt
How are the first two really any different? Are your power strips not capable of handling the load of two power supplies?

Separate powers strips provide another layer of protection.
Howso? He didn't mention surge protection/suppression, and not all strips have breakers either.

 

Mark R

Diamond Member
Oct 9, 1999
8,513
16
81
You should use a different UPS for each one of redundant supplies - so that each server is connected to 2 UPSs.

Ideally each UPS should be on a different socket outlet on a different breaker - You don't strictly need a seperate breaker for each UPS, as long as each server is connected to 2 seperate breakers via 2 UPSs.