Ok, basically I have a co-location rack with 20A of power. And it turns out I can only use 16 to 17A before tripping the circuit breaker (I don't understand why really but whatever). I'm using about 9A now. I have a storage server that I'm putting in this rack (24 750gig drives machine, and dual dual-core opteron etc.) that uses 11 amps when it powers on. It uses that much for about 5 or maybe 10 seconds, and then almost immediately goes down to about 4.5 amps.
I can handle the 4.5A sustained power, but its the spike to 20 amps that I can't. I was thinking that if I put a UPS in the rack and connect the storage to that (all four of its power supplies), will the battery absorb the load? Or since the UPS has power, will the extra load be just passed down, defeating the inteded purpose?
Oh the server has two SuperTrack EX16300 controllers, which might not be that great. Anyway, I don't think they support staggered power on, or atleast I don't see an option in their POST config tool. OR i guess I can buy a different controller but it will still probably have a power draw of 7 to 8 or 9A. Anyway some of the cheaper 1U or 2U 1500 kva UPSes are like $200 or 300 (I saw one at Frys i think). I'm just trying to keep the costs down etc. and I'd rather not pay another $200 or $300/mo for an additional 20A drop.
I can handle the 4.5A sustained power, but its the spike to 20 amps that I can't. I was thinking that if I put a UPS in the rack and connect the storage to that (all four of its power supplies), will the battery absorb the load? Or since the UPS has power, will the extra load be just passed down, defeating the inteded purpose?
Oh the server has two SuperTrack EX16300 controllers, which might not be that great. Anyway, I don't think they support staggered power on, or atleast I don't see an option in their POST config tool. OR i guess I can buy a different controller but it will still probably have a power draw of 7 to 8 or 9A. Anyway some of the cheaper 1U or 2U 1500 kva UPSes are like $200 or 300 (I saw one at Frys i think). I'm just trying to keep the costs down etc. and I'd rather not pay another $200 or $300/mo for an additional 20A drop.