Originally posted by: yellowfiero
Originally posted by: HappyPuppy
Will GFIC outlets only work with three wires? My house is very old and wired with the old cloth covered post and knob wiring. There are only two wires to each switch and outlet. Is the ground wire, the 3rd wire, necessary for a GFIC to function properly?
No, the third wire (GND) is not required. The way a GFCI works is that it compares the amount of current flowing through the hot lead, and the neutral. If they are not equal, then the difference is leaking through to ground, or through a person to ground. At a certain level, the GFCI outlet then trips, to protect the person from being shocked. As you can tell from this description, the third wire has nothing to do with it at all.
A properly wired house will have grounds available, so that chassis are grounded and provide safety by not allowing energized chassis, if an internal short occurs in an appliance. In your house, if your washer, for example, develops an internal short, the chassis may become energized, thus shocking the hell out of you when you touch it. If it had the third wire, then the chassis would have been grounded, and the short would have taken the breaker out - informing you of a problem. HTH.