- Nov 27, 2001
- 30,383
- 912
- 126
I'm strongly considering installing a 27kW electric tankless water heater to replace my existing 40 gallon electric water heater. Now, I know that gas tankless water heaters are arguably better in their throughput (about 5gpm vs. 9-10gpm), but given that I'm considering selling my place, I need to replace the water heater anyway, and the cost for an electric tankless and electric tank are not much different, I'd like to give this a shot. (I've also spoken with an old coworker that uses a 27kW electric tankless water heater, and he has no flow issues with it.)
Now, that's not really what I'm curious about, but rather I added it to provide motive. So, my issue is that I don't really have circuit space for two or three two-pole breakers right now, which is what I would need to support a larger electric tankless water heater.. My current load panel may be a 200A panel, but it's rather small in two ways... (1) it's only a 20/40 panel, and (2) it's 12" wide. From what I've read, 12"-wide panels aren't used anymore due to the lack of space between the bars, which explains why I can't find a 12"-wide panel that has more capacity. To help alleviate this, I've considered two different solutions...
1. Replace the load panel.
This is probably a task that I wouldn't tackle myself... especially since I lack a safety shut-off at the meter. I've inquired with one of those... "boutique electricians"... you know, about the equivalent of Roto Rooter. Anyway, they quoted me $5,276 to upgrade my service, which would include other upgrades to meet code. Given that I'm looking to move, it seems like a rather poor investment.
2. Add a sub panel.
This is a task that shouldn't be an issue for me to perform myself. I ran some calculations with moving my dryer (5400W), pool pump (7.5A @ 230V), and HVAC (34.7A min, 50A max), and I ended up around 90A with an additional 25% buffer. I think the only thing that makes me think twice about this idea is that it might look weird to have a sub panel placed right by your main load panel.
I've also considered whether to mount it flush right below the main load panel (it would be about 3 feet off the ground) or surface mount it to the left of the main load panel. The flush mount might look a little odd given the low height, but NEC doesn't have strict minimum heights. (You could likely argue that there is a minimum limit given this is the utility room with the washer, and water ingress would be a concern if it was closer to the floor level.) The surface mount might look nicer, but would likely require more work to run the wires.
Ultimately, it seems like #2 is the best choice, but I wouldn't mind hearing some thoughts on the matter. To note, I did consider just replacing the water heater with a normal tank unit, but I'd really like the space back in my utility room, which is already so tightly packed due to my washer and dryer being larger than what the room was ever designed for. (The house was built in the 70's.) If I could at least shift the dryer to where the current water heater is located, it would look and function so much better.
Now, that's not really what I'm curious about, but rather I added it to provide motive. So, my issue is that I don't really have circuit space for two or three two-pole breakers right now, which is what I would need to support a larger electric tankless water heater.. My current load panel may be a 200A panel, but it's rather small in two ways... (1) it's only a 20/40 panel, and (2) it's 12" wide. From what I've read, 12"-wide panels aren't used anymore due to the lack of space between the bars, which explains why I can't find a 12"-wide panel that has more capacity. To help alleviate this, I've considered two different solutions...
1. Replace the load panel.
This is probably a task that I wouldn't tackle myself... especially since I lack a safety shut-off at the meter. I've inquired with one of those... "boutique electricians"... you know, about the equivalent of Roto Rooter. Anyway, they quoted me $5,276 to upgrade my service, which would include other upgrades to meet code. Given that I'm looking to move, it seems like a rather poor investment.
2. Add a sub panel.
This is a task that shouldn't be an issue for me to perform myself. I ran some calculations with moving my dryer (5400W), pool pump (7.5A @ 230V), and HVAC (34.7A min, 50A max), and I ended up around 90A with an additional 25% buffer. I think the only thing that makes me think twice about this idea is that it might look weird to have a sub panel placed right by your main load panel.
I've also considered whether to mount it flush right below the main load panel (it would be about 3 feet off the ground) or surface mount it to the left of the main load panel. The flush mount might look a little odd given the low height, but NEC doesn't have strict minimum heights. (You could likely argue that there is a minimum limit given this is the utility room with the washer, and water ingress would be a concern if it was closer to the floor level.) The surface mount might look nicer, but would likely require more work to run the wires.
Ultimately, it seems like #2 is the best choice, but I wouldn't mind hearing some thoughts on the matter. To note, I did consider just replacing the water heater with a normal tank unit, but I'd really like the space back in my utility room, which is already so tightly packed due to my washer and dryer being larger than what the room was ever designed for. (The house was built in the 70's.) If I could at least shift the dryer to where the current water heater is located, it would look and function so much better.