electrician here.
nothing about repair vs extend or rewire in 2020 or 2023. could be in IBC or local amendments? I have studied both books as i am in night school for my masters. the only repair/extend i know of is exceptions to GFCI and AFCI protection.
15/20 amp devices: table 210.21(b)(3) , 210.21 (a) and (b)
As long as there are multiple outlets on the circuit you are quite fine to use 15a devices on a 20 amp circuit in residential construction. this is because a 20amp plug will not fit in a 15 amp outlet. so the device will be protected by its plug design. further more residential code already derates everything about 20 % in ampacity of the wire and contacts. having a 20 amp circ with 15 amp devices just makes sense when you consider that there is no limit to the number of devices on a circuit in residential construction.
Bathrooms: 210.52 (d),
now for bathrooms, the circuit can only feed one bathroom if you have lights and outlets on it, or you may feed all the outlets in all the bathrooms with one 20 amp circ if the lighting load is not on the same circ.
Splices: 334.40 (b)
in wall splices are approved where listed devices are used and may be concealed. look up the UL listing with "nonmetallic-sheathed cable interconnector devices"
NFPA 70 2023 code references ( actual name of our electrical code)
paperdoc... not sure where you get most of that, but you are mostly wrong.
If you have a circuit using 12/2 cable and fed by a 20 amp breaker, I would expect electrical code NOT to allow you to put a 15A GFCI on it. That unit is designed to handle loads up to 15 A with a modest safety factor. But the limit on the circuit imposed by the breaker is 20 A, also with a small excess allowed, so it will NOT protect the GFCI against modest and continuous overloads. I have NOT searched any local code for this detail, but it only makes sense.
nope.... a 20 amp breaker has no overhead, it will trip in less than 6ms at 20 amp, thats the standard. you should not load a breaker to more than 80% of its capacity.
In fact, the popular use of 20 A GFCI's, I suspect, is because the requirements in a kitchen were changed some decades ago. Code in our area used to require at least three Split Duplex outlets along the counter, plus a fourth near the eating table.
not even close. 2023 for a kitchen is at least 2 20 amp small applience branch circs that can not include convenience outlets. 2 feet max from end of counters and 4 feet max along countertop not to include stove opening or sink opening. all outlets in a kitchen must be GFCI protected if they are 110 to ground ( includes 240 outlets in single phase systems) no requirements for "split duplex outlets" which is a term that does not appear in code at all. 2020 was nearly the same, except for the gfci requirement for 240v outlets.
A Split Duplex is fed from a 15 A dual breaker via 14/3 cable to the mounting box bringing TWO 120 VAC lines (from opposite sides of the breaker panel) plus a Neutral.
you cant really run anymore multiwire branch circuits with gfci and afci codes. 2 hot legs with one neutral
On the outlet device the jumper on the HOT side is broken off and the two Hot lines (Black and Red) connected to those two screws which now are SEPARATE. So each of the two sockets is a separate 120 VAC 15A circuit - two 15 A circuits from a single duplex receptacle. LATER came the requirement to change so that outlets near any water (sink!) must be GFCI units and NOT simple receptacles. BUT Making a DUPLEX GFCI is tough and expensive so nobody planned to make that mandatory. So the compromise appears to be you allow on kitchen counters anywhere a 20 A GFCI with two sockets so you still can plug in two devices, but they receive from the beaker panel 120 VAC from the SAME breaker and cable and must share the 20 A current limit. MOST of the time you will not plug in and use simultaneously TWO appliances that each use close to 15 A (as the older Split Duplex system allows) so it all works. But that really is less power available from that 2-socket fixture. Personally, I'd be inclined in a kitchen to install only 15 A GFCI's, but many more of them to allow all the appliances often found along a counter. After all, so many appliances themselves are designed ONLY for 15 A max current use, and are not adequately protected by a 20 A breaker in my view.
breakers protect the wire in the wall or conduit and the devices ( a clearly defined term in NEC). They have absolutely nothing to do with anything you plug in. It's a fundamental and pervasive misunderstanding of electrical systems.
Maybe someone in the past did all that, but its not something that appears in any current code. Since 2014 the only code is 210.7 which states that if 2 or more circuits supply a single yoke ( term for one device) they must have a common trip breaker so power is turned off to both circuits if one trips. and multiwire branch circuits 210.4.