Originally posted by: Elstupido
Nameplates on motors most certainly do have amp ratings. We could get into a long discussion about Service factor, and how that affects HP ratings, and thus, amp ratings.
The start up current for a motor is already built into the circuit breaker. There are also various circuit breaker ratings which can accommodate more than normal startup currents.
Many people here do not (nor need to, on a practical basis) understand the concept of real, reactive, and apparent power. If your typical single phase, 115VAC, 2 HP motor is operating at full load, it _will_ be drawing more than (2 * 746)/115 ~= 13 Amperes. This is because your typical household induction motor is not a pure resistor. It draws reactive current because the current is out of phase with the voltage.
These subjects are why people go to university for at least 4 years. Do NOT think that just because you can fiddle around with Ohm's laws that you know all that there is to know about electrical things. You will get yourself or others hurt.
Evadman: Motor nameplates (from any respectable manufacturer) most certainly will tell you what the full load current is. You cannot determine this from the voltage and power, unless you know the power factor and how to factor that into your math. The reason why you see 5HP vacuums and the like is because at start-up the motor works at about 5HP just to get going, at the instant you turn it on. The 5HP is just a marketing number. It's a peak rating.