Loreena, you are confused like I was because Elstupido is not explaining himself well. For me, he was saying 30a rated everything EXCEPT the wall outlet. Of course that's bad since the outlet is not rated for 30 amp. But Elstupido only said 'recpticle', not '15 amp household recepticle'.
For your question, Elstupido is saying that the insulation is rated for 600 volts before breaking down (leaking voltage). You are absolutely right that voltage is very important in determining how many watts are available to an electrical system. And as you stated, the wire itself is rated for a certain amperage, and the voltage and amperage together are what matters.
you are agreeing, but explaining poorly. Long story short:
Insulation on most household wiring is rated for 600 volts
14 gauge wire is rated for a 15 amp circuit
Thus a 14 gauge wire with 600v insulation can carry 15 amps at 120v, 240v or 480v without an issue. That also means it can do 2x the amount of 'work' (measured in watts) at 15a/240 as 15a/120v. Or 4 times the work at 480v.
Originally posted by: Loreena
you can split phases with a small breakout box or distro and have two 15A 120 circuits on a single 15A double pole feed from your box.
Remember, you have to be careful in how you do that. It is against code to have 2 hots and 1 neutral of the same size, even if phase split AFAIK. Even though we all know that 2 15a circuits fed from a double pole breaker should be phase shifted 180 degrees, thus canceling out to 0a on the neutral line assuming equal load, it is still not allowed.