I am not sure what happened over night, I wasnt here...
I just walked into the house, noted the blower was blowing.. the house is frigid...
problem: the HVAC thermostat is off..there is no display and no lights on it.. no response from it. Its on the same circuit as the rooftop mounted lennox.
Any idea what it may be. Is this a failsafe for the system, thermostat blows, causes the fan to go on...? NO idea how long this has been running... it was fine when I left around 2:30 yesterday afternoon.
UPDATE: 12/31/2012
Tech came out, pulled panel, no power in system. Blower running. Runs upstairs to roof, finds no heat system going. Manually turns on the system by overriding it, works for 5 minutes fails.
Turns out a sensor failed, its an overheat sensor that failed. He's taken the sensor and will be back later in the week when he gets a replacement part. A 5 minute job for him then but yeah he was really nice.
Turns out there was some mickey mousing in the wiring. The thermostat is supposed to get power, but it turns out in cool mode if the sensor fails the AC will continue to work and the thermostat will continue to work, however in heat mode, if the sensor fails, it all stops working.. why.. well turns out the system is is wired funny.
Update: 1/12/2013
Tech came in, put a new sensor, 12 hours later it fails on over heat.. I think there is a bigger problem here. Hope that the sensor by pass did not cause my heatexchanger to crack / fail due to overheat issues. I believe its now over heating for another reason, the sensor failing was the first obvious issue, but now there is something else that needs to be looked at.
I just walked into the house, noted the blower was blowing.. the house is frigid...
problem: the HVAC thermostat is off..there is no display and no lights on it.. no response from it. Its on the same circuit as the rooftop mounted lennox.
Any idea what it may be. Is this a failsafe for the system, thermostat blows, causes the fan to go on...? NO idea how long this has been running... it was fine when I left around 2:30 yesterday afternoon.
UPDATE: 12/31/2012
Tech came out, pulled panel, no power in system. Blower running. Runs upstairs to roof, finds no heat system going. Manually turns on the system by overriding it, works for 5 minutes fails.
Turns out a sensor failed, its an overheat sensor that failed. He's taken the sensor and will be back later in the week when he gets a replacement part. A 5 minute job for him then but yeah he was really nice.
Turns out there was some mickey mousing in the wiring. The thermostat is supposed to get power, but it turns out in cool mode if the sensor fails the AC will continue to work and the thermostat will continue to work, however in heat mode, if the sensor fails, it all stops working.. why.. well turns out the system is is wired funny.
Update: 1/12/2013
Tech came in, put a new sensor, 12 hours later it fails on over heat.. I think there is a bigger problem here. Hope that the sensor by pass did not cause my heatexchanger to crack / fail due to overheat issues. I believe its now over heating for another reason, the sensor failing was the first obvious issue, but now there is something else that needs to be looked at.