Update
Voltmeter test: Only one of the "incoming" wires shows power, and it's already 240V. I think that the other wire goes off somewhere to a heater that had been removed several years ago.
Part II
Ok, I think it's all finally figured out. There is one wire coming in from the breaker box, providing 240V. It then splits off two ways - one goes directly to the thermostat and then to the heater, the other wire feeds into another thermostat in another room, which controls a different heater.
There were also remnants of the old thermostat's wiring - stranded wire wrapped around bare solid wire, and a 68K 1-or-2 watt resistor wired across somewhere, using a wire that looks to be AWG 16.
I've got two 120V lines coming to an electrical box, and a line going out to a baseboard heater. The two breakers that feed the incoming lines are ganged together.
So what I'm looking at:
- Two cables feeding power, 12 gauge, with a black, white, and ground wire each.
- One cable going out to the heater, with a black, white, and ground wire.
These wires previously connected to a thermostat, but that thermostat broke (it decided to set itself to maximum and stay that way, regardless of what the dial was set to), so it was unceremoniously removed, and the wiring was capped in wire nuts and left unused - until now.
I've got a new thermostat (SKU 442-658, in case that direct link doesn't work), and it's got instructions for either 4 wires or 2 wires. Not counting the ground, I've got 6.
So then, I think that the main thing I really need to do here is to wire the two 120V lines into a single 240V line. With that done, I should be able to use the new thermostat's 4-wire instruction set.
And an FYI, yes, I have done some wiring in the past, but only with 120V lines. I do know how to keep hot, neutral, and ground in their proper places.
Voltmeter test: Only one of the "incoming" wires shows power, and it's already 240V. I think that the other wire goes off somewhere to a heater that had been removed several years ago.
Part II
Ok, I think it's all finally figured out. There is one wire coming in from the breaker box, providing 240V. It then splits off two ways - one goes directly to the thermostat and then to the heater, the other wire feeds into another thermostat in another room, which controls a different heater.
There were also remnants of the old thermostat's wiring - stranded wire wrapped around bare solid wire, and a 68K 1-or-2 watt resistor wired across somewhere, using a wire that looks to be AWG 16.
I've got two 120V lines coming to an electrical box, and a line going out to a baseboard heater. The two breakers that feed the incoming lines are ganged together.
So what I'm looking at:
- Two cables feeding power, 12 gauge, with a black, white, and ground wire each.
- One cable going out to the heater, with a black, white, and ground wire.
These wires previously connected to a thermostat, but that thermostat broke (it decided to set itself to maximum and stay that way, regardless of what the dial was set to), so it was unceremoniously removed, and the wiring was capped in wire nuts and left unused - until now.
I've got a new thermostat (SKU 442-658, in case that direct link doesn't work), and it's got instructions for either 4 wires or 2 wires. Not counting the ground, I've got 6.
So then, I think that the main thing I really need to do here is to wire the two 120V lines into a single 240V line. With that done, I should be able to use the new thermostat's 4-wire instruction set.
And an FYI, yes, I have done some wiring in the past, but only with 120V lines. I do know how to keep hot, neutral, and ground in their proper places.