An R22 system running in a vacuum even on the low side is not normal. Those pressures would be in PSIG. R22 at +66F would be under approx 112 PSIG.
Never heard of ion heat pumps. Heat pumps need a defrost cycle because in the heating cycle the outdoor coil becomes the evaporator (opposite of air conditioning cycle) and will get below the frost point. During a defrost cycle the reversing valve is engaged (orange wire goes high) and the outdoor coil becomes the condenser. The outdoor fan is stopped as well to make the coil heat up faster. (rapid increase of head pressure)
Since the indoor coil is now the evaporator and is getting cold we don't want to blow cold air onto people (they don't like that!) so the AUX heat relay is called on to duty energizing strip heaters. Their function is to reheat the air so cold air is not felt from the registers. (it also makes your electric meter spin like crazy as 10+ kW sized strip heaters are not uncommon in a typical residential air handler with a heat pump!