The tesla wall units are basically whole house UPSs and cost only around 8k IIRC.Damn... how much would a whole house UPS cost? Sounds awesome if you live out in the boonies, but it can't be cheap.
I've always wondered what, if any, are the downsides to using online UPS vs. line-interactive. Wear and tear on the batteries? Some power loss penalty? In large data centers with both UPS and generator backup, are those UPS systems online or switched?
I've always wondered what, if any, are the downsides to using online UPS vs. line-interactive. Wear and tear on the batteries? Some power loss penalty? In large data centers with both UPS and generator backup, are those UPS systems online or switched?
Nope, what you are looking for is a called a "hardwired UPS".I am looking to put UPS on a 20 amp circuit. I want the outlets on that circuit to have the UPS protection. I don't want to use a UPS that I would plug into the outlet and then the device into that UPS.
Line in - UPS - Breaker - Load
Is that inline?
![]()
Guessing you meant online. Online or dual conversion would mean that the inverter is always running and the load is running off the inverter. The benefit of that is there is no delay between switching to battery when power goes out. With typical consumer ones they are standby, and a relay actually has to switch the output to the inverter as the AC-DC converter is strictly only for charging the battery and not powering the load. They can save money that way by not needing a beefy one.
Basically with an online UPS you have:
120vac hydro in => AC-DC converter generating DC (ex: 54v) -> battery => Inverter => 120vac UPS protected power out.
When power goes out, the AC-DC converter stops working, but the battery is in parallel with the output and connected to inverter so it then takes over immediately as it's part of the circuit. The AC-DC converter's voltage is set to float voltage which is a voltage you can set a battery at indefinitely without overcharging it.
The telcos do this, except they skip the inverter part, (well they still have inverters for some loads) as most of the equipment runs straight off 48vdc. Well it's actually a positive ground system, so it's -48vdc, but same idea.Float voltage for a 48vdc system is actually 54v. If you stick a multimeter on your phone line you'll get about that, and that's actually from the telco's batteries.
For a house, you'd do a 48vdc system with a couple large inverters that can work in parallel so that if one fails you still have power.
Good explanation. The industry buzz-phrase for the topology is "true on-line double conversion."
The company I work for has some UPS products (I'm heavily involved in them). Being able to play around with lithium-ion battery packs was a lot of fun.
Is that in front of Kaido's place? Did he order some more gadgets from Amazon for the house?
I imagine lot of UPS systems will start moving to lithium ion, but how does that work, for balance charging and using at same time? Ex: how do you both draw from, and balance charge a pack? Or do they alternate between charge/discharge using more than one pack?
With lead acid you just set it to float and call it a day, but you can't do that with lithium ion unless you want to celebrate the birth of your country and invite the fire department over for the party.![]()
I can't go into too much detail (proprietary design information and all), but the battery pack is never charged while it is in use (i.e. loss of AC or DC input power) - it is simply discharging. There is a regulated charger module that controls the charging current for the battery pack. When a valid source is present and the battery is fully charged, it is kept in a float state. When the battery is charging, the charger is drawing power from the DC bus. The system has an electronic switch module which isolates the battery from the DC bus; it connects the battery directly to the bus when the input source is down, and disconnects it when the input souce is present. Note that this is a military-grade system.
Inside the battery pack are eight 4.2V lithium ion cells arranged in series for each "tray". There are three trays in our 1U pack connected in parallel (200Whr), and seven trays in our 2U pack (500Whr). Each tray contains charge/discharge control and protection, and monitoring circuitry with additional protection (i.e. over-temperature). It's incredibly robust.