• We’re currently investigating an issue related to the forum theme and styling that is impacting page layout and visual formatting. The problem has been identified, and we are actively working on a resolution. There is no impact to user data or functionality, this is strictly a front-end display issue. We’ll post an update once the fix has been deployed. Thanks for your patience while we get this sorted.

UPS failure

MuffD

Diamond Member
I have an APC smart UPS 1400 SU1400NET Battery Backup but it won't turn on. I'm wondering if the battery pack has anything to do with it or if it's just broken. Anyone have any experience with these? I just hung up the phone waiting for APC tech support (on hold for like 30 minutes) so I thought I would ask in here.

Thanks for your help.
 
My guess is that it's broken. If the batteries were just dead, it should give you an alarm for "low battery". But since it won't come on, I'm thinking it's broke.
 
I have the same UPS, and there is an indicator that tells you if the battery is bad. If the entire front-panel does not display anything (i.e. LEDs do not light), take a look at the rear-panel and see if the "site wiring fault" indicator is on. If neither of these solves the problem, be sure that the battery is connected internally. 😉

 