So we have a few of these "2000VA/1200watt" Ultra UPS boxes at work, each one connected to 2x rack servers used for rendering. They don't last long at all during a power outage. Furthermore, one of them now keeps shutting down. Before purchasing a replacement, I want to make sure there's nothing fishy going on. It wasn't my purchase decision, but I can't find a single other "2000VA/1200watt" UPS that sells for $200. Cheapest ones I've found are:
Cheapest 2000VA/1200watt unit at Newegg (http://www.newegg.com/Product/...ult=True&Pagesize=100) = $400
Cheapest 2200VA/1500watt unit at TigerDirect, no 2000VA available (http://www.tigerdirect.com/app...c:234|&Sort=4&Recs=30) = $450
At Amazon (http://www.amazon.com/s/qid=12...2&rh=n%3A172282%2Cn%3A!493964%2Ck%3Aups+2000va&sort=price) = $515+
I did some research and came across a couple interesting white papers:
Understanding Power Factor, Crest Factor, and Surge Factor: http://www.apcmedia.com/salest.../SADE-5TNQYL_R0_EN.pdf
Watts and Volt-Amps: Powerful Confusion: http://www.apcmedia.com/salest.../SADE-5TNQYF_R0_EN.pdf
Here's one small excerpt:
"Power factor has an important implication in the specification of UPS run time on battery. Battery run time is
dictated by the watt load on the UPS. However, when many UPS manufacturers specify run time at full load
they are referring to full VA load, not the full watt load. For example, a UPS rated at 10,000 VA may be
rated for 20 minutes of run time at full load. In the fine print it notes that this full load is at a .65 power factor.
Therefore the load for the run time specification is really only 6500 Watts. The same UPS may have a 9000
W rating. This means that the run time was provided at 6500/9000 or 72% of the full load watt rating of the
UPS. At 72% of the Watt rating the UPS may run almost 70% longer than at the real full load Watt rating.
So this UPS which claimed to have 20 minutes of run time may only provide 12 minutes of run time at the
true full load Watt rating. To overcome this confusion, always make sure run time specifications are based
on Watt loads, and not VA loads."
I may be doing some real world testing with a power monitor on these, but before I spend the time, I also found this little random blurb on the net:
"the 2000VA/1200watt rating only describes the power inverter that converts the battery DC to 120 volt AC...
a 2000VA UPS doesn't necessarily last longer than a 1000VA UPS!
how long it lasts depends on how many Amp-Hours the internal battery can hold given the same usage. "
Is that accurate?
If so, are we (and everyone else) getting shafted on these "2000VA" UPS which are really no better than equally priced 1000VA APCs?
Cheapest 2000VA/1200watt unit at Newegg (http://www.newegg.com/Product/...ult=True&Pagesize=100) = $400
Cheapest 2200VA/1500watt unit at TigerDirect, no 2000VA available (http://www.tigerdirect.com/app...c:234|&Sort=4&Recs=30) = $450
At Amazon (http://www.amazon.com/s/qid=12...2&rh=n%3A172282%2Cn%3A!493964%2Ck%3Aups+2000va&sort=price) = $515+
I did some research and came across a couple interesting white papers:
Understanding Power Factor, Crest Factor, and Surge Factor: http://www.apcmedia.com/salest.../SADE-5TNQYL_R0_EN.pdf
Watts and Volt-Amps: Powerful Confusion: http://www.apcmedia.com/salest.../SADE-5TNQYF_R0_EN.pdf
Here's one small excerpt:
"Power factor has an important implication in the specification of UPS run time on battery. Battery run time is
dictated by the watt load on the UPS. However, when many UPS manufacturers specify run time at full load
they are referring to full VA load, not the full watt load. For example, a UPS rated at 10,000 VA may be
rated for 20 minutes of run time at full load. In the fine print it notes that this full load is at a .65 power factor.
Therefore the load for the run time specification is really only 6500 Watts. The same UPS may have a 9000
W rating. This means that the run time was provided at 6500/9000 or 72% of the full load watt rating of the
UPS. At 72% of the Watt rating the UPS may run almost 70% longer than at the real full load Watt rating.
So this UPS which claimed to have 20 minutes of run time may only provide 12 minutes of run time at the
true full load Watt rating. To overcome this confusion, always make sure run time specifications are based
on Watt loads, and not VA loads."
I may be doing some real world testing with a power monitor on these, but before I spend the time, I also found this little random blurb on the net:
"the 2000VA/1200watt rating only describes the power inverter that converts the battery DC to 120 volt AC...
a 2000VA UPS doesn't necessarily last longer than a 1000VA UPS!
how long it lasts depends on how many Amp-Hours the internal battery can hold given the same usage. "
Is that accurate?
If so, are we (and everyone else) getting shafted on these "2000VA" UPS which are really no better than equally priced 1000VA APCs?