That's a Tripp-Lite APS750 750w inverter-charger I got off ebay. Surprisingly hard to find an inverter-charger that does pure sine wave and can switch fast enough for computer equipment to not notice. You'd think these would be more available but they arn't. I would have rather go with 24v or 48v system though but this does the job. This one is not pure sine but it's a compromise between square and pure sine so it gets the job done. I have two 100AH marine batteries hooked up to it.
I ran a test and it ran a 300w load for about 5 hours. My initial calculation was 8h but that was without taking inefficiency and voltage drop into account. As the voltage drops, the current drawn is higher, so this makes the battery deplete faster. I was not checking often enough but my last reading was 11.1 and I noticed the systems were off maybe 15 minutes later so my guess is the shut off is at 11 volts. This is some logging I took, thought I'd share:
time voltage
1:00 12.3
1:22 12.2
2:10 12.1
2:21 12.1
3:17 11.9
3:40 11.8
4:26 11.6
4:39 11.7
5:04 11.4
5:42 11.1
Now I just need to find a way to read the voltage through my linux box so I can monitor it remotely and possibly even have an automated process that shuts down everything when it reaches 11.2 or so.
Eventually I want to get a cable crimper and ends and a roll of cable so I can make my own cables, and also a solid shelf for the unit as well as the batteries to get them off the floor in case of water issues, but for now it will do. The display of the unit is actually where the cables connect and because I could not find cables that were longer I had no choice but to place it that way.
My far future goal is a fully online high capacity (3kw or so) 48v system though but this will do for now. It's not so much that my stuff is critical, but that it is hard on the equipment to cold boot it because a lot of it is old, so I rather ride through outages and keep the disks spinning then to have them turn off. Had a 2 hour power outage the other day but this was not arrived yet. I will keep it running on my test load for a few more days then put my server stuff on it. Summer is notorious for 1-4h outages due to the construction in my area as well as the wind/storms. We had a 4h one last year that nearly killed my server. Ended up putting over 1k into it to get it going again. A typical UPS will only last a few minutes.