The central AC doesn't work so I am thinking of getting a small window AC unit. I have all my electro-gizmo toys and computers in this room and was worried about what the window AC unit might do to the power in this room. Will it cause severe changes (drops or spikes) in voltage that can damage electronics?
 

Nik

Lifer
Jun 5, 2006
16,101
2
56
You can get window AC units that will use less than 5KWh/mo.

Besides, all of your electronics should be on voltage-regulating power strips.
 

PieIsAwesome

Diamond Member
Feb 11, 2007
4,054
1
0
Originally posted by: Nik
You can get window AC units that will use less than 5KWh/mo.

Besides, all of your electronics should be on voltage-regulating power strips.

I am using surge protectors but I wasn't aware that they regulate voltage.
 

hanoverphist

Diamond Member
Dec 7, 2006
9,867
23
76
Originally posted by: PieIsAwesome
Originally posted by: Nik
You can get window AC units that will use less than 5KWh/mo.

Besides, all of your electronics should be on voltage-regulating power strips.

I am using surge protectors but I wasn't aware that they regulate voltage.

usually they will regulate the over side, but i dont recall them ever maintaining voltage if the supply drops... if you want to clean that up, get a UPS to supply all the toys. the start up may spike it up, but as long as you arent at your 15a limit, shouldnt be an issue.
 

MotF Bane

No Lifer
Dec 22, 2006
60,801
10
0
I'll check tonight. I have a 5000 BTU window AC hooked into a P3 Kill-A-Watt. Wattage ramp-up is pretty steady, but I haven't bothered to look at voltages.
 

Paperdoc

Platinum Member
Aug 17, 2006
2,381
310
126
The problem an AC can create for electronic units is that, for a few seconds as it starts up, the AC motor pulls a huge current and that can drop the voltage because of resistance in the wall wiring. That resistance is normal (unless there is a real wiring flaw.) So some electronics experience voltage sag for a few seconds every time the AC starts. The second, less likely situation comes up if your circuit already is heavily loaded. In those cases the start-up current just might push the total circuit load over the limit and cause the breaker to trip out. Then your electronics experiences a complete power failure. If that happens just when certain tasks are under way (such as a disk write) you will see damage in the form of corrupt files, etc.

A Surge Protector does not help this - it's designed for fast high voltages, not sags. The UPS suggestion would do it. If all you want is protection from short voltage sags, a smaller unit that does not keep things going for a long time is OK. Just be sure it is the type that is always supplying power, not the old type that switches itself over after the power fails.

The other alternative is to set the AC up on a separate circuit (preferably with little other load on it). You'd need to find an outlet that does not turn on and off when you trip the breaker for your electronics units. You might need to run a heavy-duty extension cord (one that says it can handle an AC) to reach that outlet. The advantage is that the heavy current pull and resulting voltage sag will happen on different wall wiring. It is unlikely the voltage will be pulled down at the bus inside the breaker panel, so you would prevent causing the problem where your electronics are plugged in.
 