is this normal for house radiator?

luv2liv

Diamond Member
Dec 27, 2001
3,505
95
91
with a thermal camera, i can easily see the radiator is hot near the top. i thought it would be more evenly distributed. so is this normal?

PRq0YML.jpg



with normal light, it looks something like this:
Depositphotos_2371041_s-2015.jpg
 

boomerang

Lifer
Jun 19, 2000
18,883
641
126
Heat rises. At some point the steam must cool enough in order to return to the boiler as water. A radiator therefore cannot not be uniformly the same temperature.
 

Billb2

Diamond Member
Mar 25, 2005
3,035
70
86
That's a weird (cheep) setup. There's no condensate return line (back to the boiler), and no air vent. The steam (hot) coming into the radiator is cooled by the condensate (cold) returning through the same pipe. And without an air vent the top of the radiator is filled with air. Whatever steam makes it to the radiator just turns into water vapor (warm) at the top of the radiator. It's just wrong. But, it you're getting enough heat for the room and you don't pay the heating bill who cares. It's just very inefficient and expensive to run that way.
 

hdfxst

Senior member
May 13, 2009
851
3
81
move the cover away from the radiator and then look at it.What your seeing in the pic is the temp of the screen on the cover and not the radiator
 

paperfist

Diamond Member
Nov 30, 2000
6,539
287
126
www.the-teh.com
That's a weird (cheep) setup. There's no condensate return line (back to the boiler), and no air vent. The steam (hot) coming into the radiator is cooled by the condensate (cold) returning through the same pipe. And without an air vent the top of the radiator is filled with air. Whatever steam makes it to the radiator just turns into water vapor (warm) at the top of the radiator. It's just wrong. But, it you're getting enough heat for the room and you don't pay the heating bill who cares. It's just very inefficient and expensive to run that way.

Air vent is on top left, but it's manual.

That does seem to be an odd setup, I always thought the water had to circulate. Not sure how that's accomplished without a return line. Maybe that's why all the heat is up top.
 

luv2liv

Diamond Member
Dec 27, 2001
3,505
95
91
yeah, the thermal pict is with a metal cover on top.
let me post something else later
 

NetWareHead

THAT guy
Aug 10, 2002
5,847
154
106
Isn't that kind of a low temp?
The camera measures the temperature of the radiator surface, not of the steam inside the radiator. The steam inside is surely > 212 F. It looks like that radiator has just begun heating. It takes a while for that entire mass of cast iron to heat up. You can see in this thermal image the steam entering from the bottom left and rising to the top.
4e8bb1dc477a9-.jpg


I never thought about that, but it does seem low. I also don't see an out let pipe, though it has to be there somewhere.
This is a 1 pipe steam system. It relies entirely on the buoyant effect of hot steam to move energy throughout the system. Nowadays with electric circulators (hot water hydronic heat systems), steam powered energy transfer systems are a lost art. The radiator itself is slightly pitched down at the steam riser end. When steam cools, water condensate forms on the bottom and the pitch of the radiator allows it to run off and back into the steam riser and ultimately back towards the boiler for reuse.

2 pipe steam systems also exist with dedicated supply and return pipes. The radiator air vent in the room is also eliminated in this type of system.
 
  • Like
Reactions: paperfist

Greenman

Lifer
Oct 15, 1999
22,326
6,480
136
I've done several split hydronic systems, and one that used radiators, but I've never seen an actual steam heat system. Any idea what pressure they run at?
 

NetWareHead

THAT guy
Aug 10, 2002
5,847
154
106
I've done several split hydronic systems, and one that used radiators, but I've never seen an actual steam heat system. Any idea what pressure they run at?

Not more than a few pounds of pressure, if that. Most buildings heat well with 2 PSI of steam pressure. Steam packs far more energy than hot water and wants to actively expand to areas of low pressure as it seeks to equalize. Its a different animal than hydronic; one of my hydronic boilers has a pressure relief valve that blows at 25 PSI. . Read in some old steam manuals once that 1 PSI is enough to move steam upwards 2/3 of a mile.
 

paperfist

Diamond Member
Nov 30, 2000
6,539
287
126
www.the-teh.com
The camera measures the temperature of the radiator surface, not of the steam inside the radiator. The steam inside is surely > 212 F. It looks like that radiator has just begun heating. It takes a while for that entire mass of cast iron to heat up. You can see in this thermal image the steam entering from the bottom left and rising to the top.
4e8bb1dc477a9-.jpg



This is a 1 pipe steam system. It relies entirely on the buoyant effect of hot steam to move energy throughout the system. Nowadays with electric circulators (hot water hydronic heat systems), steam powered energy transfer systems are a lost art. The radiator itself is slightly pitched down at the steam riser end. When steam cools, water condensate forms on the bottom and the pitch of the radiator allows it to run off and back into the steam riser and ultimately back towards the boiler for reuse.

2 pipe steam systems also exist with dedicated supply and return pipes. The radiator air vent in the room is also eliminated in this type of system.

So water doesn't really circulate back to the boiler it basically is continually heated? I don't quite understand how it does that with low pressure.
 

NetWareHead

THAT guy
Aug 10, 2002
5,847
154
106
So water doesn't really circulate back to the boiler it basically is continually heated? I don't quite understand how it does that with low pressure.

Meghan54 posted a good diagram of a 1 pipe steam system. Steam is pushed to all boundaries of the system by pressure, even uphill. Leaves the boiler via the steam header and reaches different rooms by branch piping. Condensate is created when steam has given up it's heat in the radiator and flows back to the boiler via gravity. The piping system is a 2 way street if you think about it. Steam flows one way pushed uphill by pressure. Condensate flows in the opposite direction via gravity and every pipe is pitched to allow condensate to drain back towards the boiler for reheating back into steam. One pipe steam systems use larger piping than 2 pipe systems since the piping needs to allow for this 2 way traffic. 2 pipe systems have dedicated steam feeds and condensate returns for each radiator and the pipe sizes are smaller as a result.

This is why piping pitch, pipe size and any obstructions interfere with steam delivery/condensate return and create issues like noisy water hammer, excess fuel consumption and rooms that get no heat. IMO these systems are works of art that function entirely without moving parts; no circulators needed. Just steam pressure and gravity work to provide a reliable circulatory effect. Much like a mechanic that can tune a carburetor, the long dead plumbers who installed these systems knew their craft well. That's why I called it a lost art.
 

luv2liv

Diamond Member
Dec 27, 2001
3,505
95
91
as promised, here are the photos without the cover: https://imgur.com/a/FJnL8
so it looks like my radiator is probably working well after all because heat is evenly distributed as i thought!

sslKifh.jpg



left side is where hot water enters the 1 pipe into the radiator. cooler water (20 degrees difference) exits on the right pipe, with a valve on top. i have no idea what the valve does!
a nuisance i have is the 1st floor being cold, around 68F. while the second floor is really hot, 79F. the 2nd floor is hotter because the rooms are smaller with at least 2 radiators per room! i've turned the valve clockwise to close but the radiator is still hot as before. i tried counter clockwise too but no dice. any idea on how to reduce the heat on the 2nd floor without the 1st floor being colder? would be nice if the 1st and 2nd come close to each other at 73F.
 

NetWareHead

THAT guy
Aug 10, 2002
5,847
154
106
You have a 2 pipe steam system which is great for you because they are supposed to be configurable and easier to balance (balance as in adjust each room) than 1 pipe systems. The valve on the radiator is supposed to to allow you to adjust the flow of steam. If nothing happens when closing the valve, you may need to replace.

Also, give the radiator some time to shed its heat after you try closing the valve. That radiator needs like 30+ minutes to return to normal. If the valve is not letting you close the steam off, you might want to get a plumber in there to replace it.

I'm also surprised to see the valve on the return side. Usually the valve is on the supply side in 2 pipe systems. If my suspicion is correct, closing the valve will still allow steam to enter the radiator.

Lets make sure for a second. You have steam and not hot water system, correct? Does your boiler have a sight glass that shows you the boiler water level? Do you have any circulators near the boiler?
 

luv2liv

Diamond Member
Dec 27, 2001
3,505
95
91
Lets make sure for a second. You have steam and not hot water system, correct? Does your boiler have a sight glass that shows you the boiler water level? Do you have any circulators near the boiler?

i believe it is hot water. fthere is no glass anywhere near radiator.
each bedroom has 2 radiators connected serial. im thinking of removing 1 of the radiator. since it is serial, i cant just remove 1 and cap the pipes. im thinking of removing a radiator and just connect a copper pipe straight through. then build a bookshelf of the hot pipe to prevent kids touching that copper pipe. good idea?
 

Greenman

Lifer
Oct 15, 1999
22,326
6,480
136
i believe it is hot water. fthere is no glass anywhere near radiator.
each bedroom has 2 radiators connected serial. im thinking of removing 1 of the radiator. since it is serial, i cant just remove 1 and cap the pipes. im thinking of removing a radiator and just connect a copper pipe straight through. then build a bookshelf of the hot pipe to prevent kids touching that copper pipe. good idea?
You could also put a thermostat in the room and a valve at the supply end, have a zoned system.
The only hot water/radiator system I ever installed was done that way. I put a stat in every room that had a radiator, each stat controlled the valve for that loop. The owner loved the system.
 

NetWareHead

THAT guy
Aug 10, 2002
5,847
154
106
i believe it is hot water. fthere is no glass anywhere near radiator.
each bedroom has 2 radiators connected serial. im thinking of removing 1 of the radiator. since it is serial, i cant just remove 1 and cap the pipes. im thinking of removing a radiator and just connect a copper pipe straight through. then build a bookshelf of the hot pipe to prevent kids touching that copper pipe. good idea?

Radiators connected in serial are almost always hot water. Steam radiators are connected in parallel (bad installs are the exception).

The sight glass would be on the boiler, not in the room. The circulators would be on the boiler.

Re your bookshelf idea, better idea would be to wrap pipe insulation around it before building a shelf.