The quality of today's UTP, coupled with better transceiver technology and design, minimize that kind of interference to a vitrual nil.
One foot from an AC source is no big deal. It would be nearly impossible to run cabling today and NOT be within one foot of SOME kind of AC souce along the way. All Category-rated cabling is good for ~100 meters (~108 Yards, ~325 feet) shielded or not. Unshielded Category-rated cabling meets exactly the same specs as the Shielded stuff (same Cat spec).
I can pretty much guarantee that improperly terminated shielded cable (or a mix of shielded and unshielded components on shielded cabling) will do you much worse. It will be no better than common phone wire (no Category rating), probably worse ... depending on how / how much you violate the specs.
For example, if you do not ground the shield properly, the shield will act as an antenna and collect common-mode noise (60 Hz). If you don't ground it properly (single point to the facilities ground), you run the risk of a ground loop and enhanced 60Hz (and other environmental noise) collection.
Keep in mind that shielded cable (actually "Shielded" UTP is called "Screened" (because otherwise you'd have "Shieled Unshielded Twisted Pair") was designed and built for that screening to assist in reducing the interference .... even if the (improperly terminated) shielding didn't contribute to the noise reduction, the wire pairs within are not built to a configuration that can function as welll as cabling designed to work without shielding.
Screened / shielded cabling also operates at a different impedence (~120 - 150 ohm versus ~100 for UTP). You losses / attenuation will be higher if not properly terminated (reduces the ACR - Attenuation-to-Crosstalk Ratio - a very bad thing).
IMHO, If you've already run the cabling, your best bet is to use it to pull in standard UTP of whatever Category rating you desire. The cost difference in components and potential performance problems aren't worth whatever you already spent.
FWIW
Scott