lol, 8 figure... really? its not a govt project. I am guessing higher 6, 700k maybe?
I can't even guess how much this equipment costs, thus the question.
lol, 8 figure... really? its not a govt project. I am guessing higher 6, 700k maybe?
Out of curiosity, how expensive is a project like this? 7 figures, 8?
I'm led to believe it's in the low-mid 7 figures range.
2 New transformers, new generator, construction work for new substation/generator, architects fees, electrical design and consultancy fees
New switchgear, redesign and rewiring of an large building
Dual redundant UPSs - these alone are nearly $1million.
Excavation of roads for new HV cable installation.
Contribution to the construction of the new power company substation (split between a bunch of other customers who also need improved redundancy or more capacity).
lol, 8 figure... really? its not a govt project. I am guessing higher 6, 700k maybe?
Glenn1 is looking for a construction estimator with your skills.
http://forums.anandtech.com/showpost.php?p=36769084&postcount=114
Thought I'd post another update.
The contractors had brought a massive load bank on site by the electrical building, and it was running most of the day. Not quite sure what they were testing, because the generators weren't running.
A dude was also going round with a camera, possibly a FLIR camera.
I'm not sure what was happening. But I'm guessing that the new switchboard and/or new transformer has been installed, and is being tested before the main building is transferred over to the new switchboard.
Also, I walked the other way off site, taking the scenic route, and a massive (about 10 foot tall with massive fans) new transformer had appeared behind a small warehouse on the corner of the campus. I'm guessing that this is part of the power company's infrastructure upgrade to support the increased service to the hospital.
Thought I'd post an update. The work is now complete.
Everything has been fully tested, dual-fed, both generators and UPSs tested, including a full "blackout test", which included a UPS shutdown, so that the new SOPs for total electrical failure could be tested.
No load banks were installed, but grid paralleling switch gear was installed on the generators, so that for testing purposes, they can synchronise with the grid, and be tested at whatever load is desired without the need for either a load bank, or for a power interruption.
New fuel tanks were installed which hold 200 hours of fuel.
Summary:
Service upgraded from 1 MVA to dual-redundant 2 MVA supplies.
Second supply comes from a new power company substation which is itself supplied from a different bulk supply substation.
Single 500 kVA low power generator supplemented by a new 1.2 MVA generator.
Generators now have paralleling switchgear to allow planned switching between mains and generator without power interruption.
Dual redundant UPSs for most circuits (with the exception of stuff like non-critical HVAC, etc.)
Main switchboards, sub-boards and some final panels upgraded to dual feed to mitigate against cable failure, or failure of a main switchboard.
ICU and ORs upgraded to IPS (isolated power supplies) supplies to mitigate against short-circuit faults to ground (as the supply is isolated, a hot-to-ground fault is not dangerous on its own and will not blow fuses/trip GFCIs/etc. Instead of disconnecting the power a fault will trigger an alarm, allowing the faulty equipment to be taken out of service in a controlled manner).
it would have been cheaper to build a new hospital with these specs instead of upgrading the old one.
it would have been cheaper to build a new hospital with these specs instead of upgrading the old one.