The framing of the addition where the Ethernet comes in is metal. I'm still gonna ground to the metal electrical gang box, but just for future reference, does this mean under that code it is not recommended to ground to the metal framing if the ground is the pipe?This typically is not code and can be considered dangerous. Structure should have either 1 ground point or multiple that are all grounded together (dedicated ground wire 'structure' doesn't count.)
NEC 250.50:
NEC 250.50 All grounding electrodes that are present at each building or structure served shall be bonded to-gether to form the grounding electrode system.
NEC 250.50 Electrodes include a metal underground water pipe in direct contact with earth for 10 feet or more, a metal frame of a building or structure, a concrete encased electrode or a ground ring.
NEC 250.66 The size of the grounding electrode conductor shall be determined by the size of the service-entrance conductors, per the chart:
Code:Equivalent Size of Service Entrance Conductor Size of Grounding Electrode Conductor Copper Aluminum Copper 4 AWG 2 8* 1 AWG 2/0 6 2/0 or 3/0 4/0 or 250 4
There is a ton more but I don't feel like typing all of 250.50 out as it is rather long. The key thing about pipe grounding is that the ground point is actually the ground for the piping system and not technically a structure ground. They also forbid using the pipe itself as a multiple ground point for reasons stated above.
Cuz if the electrical boxes are all fastened to the metal framing wouldn't that mean it's all electrically bonded anyway?