Circuit has 110v-120v but seems no current?

mxnerd

Diamond Member
Jul 6, 2007
6,799
1,103
126
My two backyard post lights with power sockets near the base all of a sudden would not light up and nothing will turn on when I plug in portable lights or power tools.

I suspect that it rained a lot last month and probably the post lights short circuited somehow. I replaced the rusty sockets & switches and still no go.

I measured the voltage on the socket's silver & black screws / white & black wires and it's 110-120v, but nothing will turn on, it seems there is no current, what's going on?

The portable lights and power tools work perfectly everywhere else.

Thanks.
 
Last edited:

stormkroe

Golden Member
May 28, 2011
1,550
97
91
You can have an effective break in your circuit and have full voltage with no practical current. A bad breaker, burnt splice, etc can be the culprit. Maybe the socket tab is burnt/bent?
 

mxnerd

Diamond Member
Jul 6, 2007
6,799
1,103
126
I replaced the old sockets with brand new ones so no bent/burnt tabs.

I also sanded the splices a little with sandpaper so no burnt / oxidized splices.

The two pole lights are actually #3 & # 4 downstream.

#1 outer wall sockets and #2 sockets in the middle worked perfectly so no breaker problem.
 

mxnerd

Diamond Member
Jul 6, 2007
6,799
1,103
126
Forget to mention #1 is a GFCI socket. Does that make any difference? #1 & #2 work fine and have electricity though.
 

mxnerd

Diamond Member
Jul 6, 2007
6,799
1,103
126
When I plugin the portable CFL light, the voltage on the screws drop to 12v-14, is that normal? If not, what would be the cause?

The wires between pole lights are buried in the soil inside a PVC pipe, should I dig it up and check?
 

stormkroe

Golden Member
May 28, 2011
1,550
97
91
Say WHAT?
*effective* break. If you have even 1 strand of 36ga fine strand left touching you'll get full voltage, but no useable current. Usually it will burn through if you try in that circumstance. More likely it's a burnt splice with contact through the oxide/melted insulator. Again, enough to read voltage but not enough current to meet the load (think of an undersized isolation transformer). OP, try checking connections at #1 and #2. Also, perhaps #2 is on the line side of the gfi, and the others are on the load side of the gfi and the internals are screwy.
 

mxnerd

Diamond Member
Jul 6, 2007
6,799
1,103
126
*effective* break. If you have even 1 strand of 36ga fine strand left touching you'll get full voltage, but no useable current. Usually it will burn through if you try in that circumstance. More likely it's a burnt splice with contact through the oxide/melted insulator. Again, enough to read voltage but not enough current to meet the load (think of an undersized isolation transformer). OP, try checking connections at #1 and #2. Also, perhaps #2 is on the line side of the gfi, and the others are on the load side of the gfi and the internals are screwy.

You were right! It's burnt splice at #2, which outfeeds to #3 & #4.

Respliced the wires & now it's working! Thank for the tips!!!

Best,
 
  • Like
Reactions: stormkroe

SinfulWeeper

Diamond Member
Sep 2, 2000
4,567
11
81
Sounds like a bad breaker. Perfect stunning material. Like stun guns. 1 million volts but no amps. Otherwise there would be a lot of bacon on them streets.
 

feralkid

Lifer
Jan 28, 2002
16,890
4,996
136
*effective* break. If you have even 1 strand of 36ga fine strand left touching you'll get full voltage, but no useable current. Usually it will burn through if you try in that circumstance. More likely it's a burnt splice with contact through the oxide/melted insulator. Again, enough to read voltage but not enough current to meet the load (think of an undersized isolation transformer). OP, try checking connections at #1 and #2. Also, perhaps #2 is on the line side of the gfi, and the others are on the load side of the gfi and the internals are screwy.



I see!

That makes perfect sense; I was thinking about it incorrectly.

Thank you!