Pretty sure the OP doesn't still have the problem after 3 years.
admin allisolm
Sorry if there's a lot of info here guys...I tried to make it detailed to see if I could get some assistance on what the issue may be.
- Fan stays on
- Thermostat doesn't control the unit (heating...can't test cooling)
- Condenser kicked on
Ok, so I've been having some heating issues as of late and I have to turn the thermostat up to like 80 for it to even get a decent temp in the house and even then, sometimes it'll say its 75 when it's clearly closer to 60 so...I thought I'd try a new thermostat before calling in a pro.
I bought a Honeywell RTH8580WF (WiFi, touch-screen) to replace the aging digital thermostat (I don't recall the brand/name), but I ran into an issue.
The old one is a 4-wire setup but the furnace does have a 'C' jumper.
After I set this up (with the Green = C configuration outlined below), The unit fired right up, but...once I turned it off at the Thermostat it didn't actually turn off.
After awhile it did kick-off (not sure why) and then my condenser kicked on (luckily I was sitting very close to the 'kill switch' for the furnace as it was like 12 F outside. ^_^
So for now, I've given up and placed the original Thermostat back on and switch my wiring back to the original.
So I had it hooked up like so:
From what I've found, I can:
1. Move 'G' wire to 'C' slot on Thermostat
2. Move 'G' wire to 'C' slot on Furnace
3. Add jumper from 'G' to 'Y'
In doing this, you lose the ability to run JUST the fan (so it'll be Auto at all times and kicks on with the unit).
OLD Thermostat Wires
Furnace Board Wires
admin allisolm
Sorry if there's a lot of info here guys...I tried to make it detailed to see if I could get some assistance on what the issue may be.
- Fan stays on
- Thermostat doesn't control the unit (heating...can't test cooling)
- Condenser kicked on
Ok, so I've been having some heating issues as of late and I have to turn the thermostat up to like 80 for it to even get a decent temp in the house and even then, sometimes it'll say its 75 when it's clearly closer to 60 so...I thought I'd try a new thermostat before calling in a pro.
I bought a Honeywell RTH8580WF (WiFi, touch-screen) to replace the aging digital thermostat (I don't recall the brand/name), but I ran into an issue.
The old one is a 4-wire setup but the furnace does have a 'C' jumper.
After I set this up (with the Green = C configuration outlined below), The unit fired right up, but...once I turned it off at the Thermostat it didn't actually turn off.
After awhile it did kick-off (not sure why) and then my condenser kicked on (luckily I was sitting very close to the 'kill switch' for the furnace as it was like 12 F outside. ^_^
So for now, I've given up and placed the original Thermostat back on and switch my wiring back to the original.
So I had it hooked up like so:
Red = R (RC jumpered to R (there is no RH on this one but was on the old one)
White = W
Blue = Y
Empty = G
Green = C
From what I've found, I can:
1. Move 'G' wire to 'C' slot on Thermostat
2. Move 'G' wire to 'C' slot on Furnace
3. Add jumper from 'G' to 'Y'
In doing this, you lose the ability to run JUST the fan (so it'll be Auto at all times and kicks on with the unit).
OLD Thermostat Wires

Red = RC/RH (bridged)
White = W
Blue = Y
Green = G
Furnace Board Wires

Red = R
W = White
Y = Blue (Red to AC)
G = Green
C = (White to AC)