Hello, can someone tell me how do I change a two prong to a three prong electrical outlet? All of the guides I searched for only change from three prong to three prong. I don't know what to connect the green grounding screw to. Can anyone help? Thanks
 

BigJ

Lifer
Nov 18, 2001
21,330
1
81
If you want to take the easy way out, just install a GFCI. Otherwise you'll have to run a grounding wire to the outlet.
 

Scarpozzi

Lifer
Jun 13, 2000
26,391
1,780
126
Originally posted by: BigJ
If you want to take the easy way out, just install a GFCI. Otherwise you'll have to run a grounding wire to the breaker box/fuse panel.

Fixed.

 

njmodi

Golden Member
Dec 13, 2001
1,188
1
71
Need more info - is there conduit to the junction box (metal) or is it just 3-wire romex?
 

akubi

Diamond Member
Apr 19, 2005
4,392
1
0
you can stick that green thing under the screw that holds the plastic outlet casing. unscrew it a little, slide it in and rescrew.
 

mugs

Lifer
Apr 29, 2003
48,920
46
91
If you're lucky it will be armored cable running back to the break box, in which case you can use that to ground it (just attach the other two wires, the outlet will be grounded through the outlet box).

That's how it was in our house (I've tested the outlets to ensure that they actually are grounded)
 

iRONic

Diamond Member
Jan 28, 2006
8,277
3,587
136
Originally posted by: akubi
you can stick that green thing under the screw that holds the plastic outlet casing. unscrew it a little, slide it in and rescrew.

Ahahahaha!!

 

BigJ

Lifer
Nov 18, 2001
21,330
1
81
Originally posted by: Scarpozzi
Originally posted by: BigJ
If you want to take the easy way out, just install a GFCI. Otherwise you'll have to run a grounding wire to the breaker box/fuse panel.

Fixed.

I figured he'd be able to figure out where to run the grounding wire from (the box) to the outlet. Clarification never hurts though.
 

Scarpozzi

Lifer
Jun 13, 2000
26,391
1,780
126
Originally posted by: BigJ
Originally posted by: Scarpozzi
Originally posted by: BigJ
If you want to take the easy way out, just install a GFCI. Otherwise you'll have to run a grounding wire to the breaker box/fuse panel.

Fixed.

I figured he'd be able to figure out where to run the grounding wire from (the box) to the outlet. Clarification never hurts though.
I figured you'd figure that, but on ATOT, we all have to feel important and add our .02. :D
 

Paperdoc

Platinum Member
Aug 17, 2006
2,476
363
126
In order to install a 3-prong outlet you MUST first be sure there is a good ground connection to the box in the wall. That could be from a bare copper ground lead in the cable, or from a solid conduit system all the way back to the breaker box (not likely), or from a BX cable (the ones with spiral-wound flexible steel covering over the wires) also properly connected to ground back at the breaker box. (Could be a fuse box, though, if you have 2-prong outlets.) At the breaker (fuse?) box there MUST be a ground point that is connected to a solid earth ground - a dedicated buried ground rod outside, or maybe just a heavy copper wire connected to the cold water line entering the house. Without the reliable ground all the way to the outlet box the 3-prong outlet is useless - it is NOT doing its job, but it fools you into thinking it is!

A GCFI is NOT a substitute for a proper ground. I will do only a part of the job.

On all 3-prong outlets I have seen there is an obvious green screw in the metal frame of the device - the same metal frame that mounts the device into the box with two screws top & bottom. IF you have a proper separate ground lead, it connects to this green screw. If not (if you're relying on conduit or BX cable which provides a ground to the BOX itself, then just mounting the device into the box is supposed to make the ground connection for you.

You MUST be sure the two power wires are connected to the right terminals on the outlet device. First you need to know which is which. On modern systems the wires in the cable are color-coded. They should always be black for "Hot" coming from the fuse or breaker, and White for "Neutral" coming from a common neutral bus in the breaker box. Most systems I have worked with are "Grounded Neutral" - that is, at the breaker box AND at the supply transformer outside the neutral line is grounded. (More on that in a minute). IF you are working with a Grounded Neutral system but the wire color coding is not clear, you can use this to test. Measure voltage from one wire to a true ground. The Neutral line should not have a measureable voltage on it; the Hot line will show 120 volts AC to Ground. WARNING: if both lines show voltage from a true Ground, you DO NOT have a "Grounded Neutral" system!

Now, take the new outlet device you plan to hook up. Turn it so that you are looking at the front of it as if you are ready to plug something in. Now turn it so that, on each half, the round Ground hole is at the bottom, and the two parallel flat slots are above that. There are screw terminals on each side for the power leads. The "Hot" (black) lead must go to the one on your right, and the "Neutral" (white) to your left.

Back at the breaker box, as I said, the Neutral bus will be grounded in a "Grounded Neutral" system. However, do NOT ever treat the Neutral bus or any white wires as Grounds!!! Because the white "Neutral" lines in each circuit are carrying the current back to the box, these lines have voltages on them in normal use and cannot be considered grounds points. A proper Ground (e.g., the bare wire in the cable) never has a current or voltage on it in normal operation. Under abnormal conditions (for example, a wire shorted out to the chassis in the appliance) it is required to carry a full load current safely to Ground with no interference. This will do two things: ensure the appliance case actually does not have a dangerous voltage on it to hurt you, and hopefully ensure that enough current is pulled that the breaker (or fuse) will blow out. Neither of these two protection systems can work if there is no true reliable Ground lead to the outlet box.
 

DrPizza

Administrator Elite Member Goat Whisperer
Mar 5, 2001
49,601
167
111
www.slatebrookfarm.com
Originally posted by: Scarpozzi
Originally posted by: BigJ
Originally posted by: Scarpozzi
Originally posted by: BigJ
If you want to take the easy way out, just install a GFCI. Otherwise you'll have to run a grounding wire to the breaker box/fuse panel.

Fixed.

I figured he'd be able to figure out where to run the grounding wire from (the box) to the outlet. Clarification never hurts though.
I figured you'd figure that, but on ATOT, we all have to feel important and add our .02. :D


Maybe I'm different, but I'd start at the breaker box and work my way to the outlet.
My 2 cents. ;) :p
 

chrisms

Diamond Member
Mar 9, 2003
6,615
0
0
Stick a fork in the outlet to loosen up the jacks and then proceed with the other advice given here.
 
Nov 5, 2001
18,366
3
0
if your house is old enough to not have grounded outlets, it likely only has 2 wire wiring. A 3 prong outlet will not be grounded should you install it since there is no 3rd wire. Thats why the screw has nothing to connect to. And the vast majority of homes do not have rigid conduit.

Your only choice is to run a ground wire if you want it grounded.
 

imported_Imp

Diamond Member
Dec 20, 2005
9,148
0
0
Originally posted by: MikeyIs4Dcats
if your house is old enough to not have grounded outlets, it likely only has 2 wire wiring. A 3 prong outlet will not be grounded should you install it since there is no 3rd wire. Thats why the screw has nothing to connect to. And the vast majority of homes do not have rigid conduit.

Your only choice is to run a ground wire if you want it grounded.

That about covers it. However, if you google the topic, you'll find half-assed, uninsured (probably) methods to ground an outlet by attaching a ground wire to the outlet box or water pipe. Chances are, you don't have a ground wire as there should already be a 3 pronged outlet if there were.
 
Nov 5, 2001
18,366
3
0
Originally posted by: Imp
Originally posted by: MikeyIs4Dcats
if your house is old enough to not have grounded outlets, it likely only has 2 wire wiring. A 3 prong outlet will not be grounded should you install it since there is no 3rd wire. Thats why the screw has nothing to connect to. And the vast majority of homes do not have rigid conduit.

Your only choice is to run a ground wire if you want it grounded.

That about covers it. However, if you google the topic, you'll find half-assed, uninsured (probably) methods to ground an outlet by attaching a ground wire to the outlet box or water pipe. Chances are, you don't have a ground wire as there should already be a 3 pronged outlet if there were.


yes. and as you said, these methods are very unreliable and will not provide suitable grounding
 

MedicBob

Diamond Member
Nov 29, 2001
4,151
1
0
Ummm, Armored ROMEX was used for many years and still is in some applications. IF, notice big IF, it is armored cable with 2 wire the armor might be the ground. You would need to check it and if it isn't a ground wire would need to be run.

Best bet, get an electrician and follow their advice, not the majority here as the electrician can actually see what you have.