Ac stalling with newly installed Nest termostat.

Xellos2099

Platinum Member
Mar 8, 2005
2,277
13
81
Long story short, around a month about my townhouse we changed out the condenser and installed nest as thermostat and it was good. It took longer to cool the house but ti work. A few days ago, we noticed temperature is hotter than usual. We set the ac to 72 degree but it was closer to 76. Today I decide to have a good look, while nest say it is cooling the condensor was not running. To be more precise, when I check earlier, it run for a few minute and then turn itself off. It is like the ac is stalling. I am not sure if it is the condensor issue or it is the nest. since we change both it is hard to know but it seems the nest ac stalling is not all that uncommon
 

boomerang

Lifer
Jun 19, 2000
18,883
641
126
Situations like these are why I always keep the old thermostat around for awhile after replacing it.
 

ch33zw1z

Lifer
Nov 4, 2004
39,045
19,739
146
Verify your Configuration on nest website, open a ticket with them, in the mean time Google your problem and see how others fixed it
 

NutBucket

Lifer
Aug 30, 2000
27,119
613
126
Perhaps its some odd coincidence and there's some other issue with your HVAC system preventing it from operating normally (low freon, perhaps?)
 

Zorba

Lifer
Oct 22, 1999
15,613
11,254
136
Kind of sounds like an overheat switch or liquid carry over switch opening.

If you are good with a multimeter, you can check for voltage on the single wire from the furnace going into the condenser. If it is being told to run, you should have voltage (24 Vdc, IIRC). If you have voltage on the control wire, then the problem is at the condenser, if you don't the problem is in the thermostat or furnace.
 

Red Squirrel

No Lifer
May 24, 2003
69,720
13,339
126
www.betteroff.ca
I would check for 24vac at the compressor for the relay just to rule out the thermostat. If you get 24v then it's probably a coincidence and it's another issue. If you get a lower oddball voltage, I'm almost wondering if somehow the nest is loading the transformer hard due to an odd fault and the relay is not getting quite enough voltage to stay on.
 

piasabird

Lifer
Feb 6, 2002
17,168
60
91
I have a fairly new furnace/air conditioner. The unit has a circuit board in it that has something called a limit switch. If I used an air filter like one designed to take out more dust or a HEPA filter, what would happen is the air limit switch would shut off the furnace. So I went back to the old ratty green filters. The better air filter actually slowed down the furnace airflow below acceptable limits. This makes the air limit switch go off and shut off my furnace. Try an air filter with better air flow.
 
  • Like
Reactions: Ken g6

NutBucket

Lifer
Aug 30, 2000
27,119
613
126
This is good advice for any hvac system. Use a super shitty filter. The "good" filter will decrease airflow to the point it effects efficiency. Bad idea.
 

gorcorps

aka Brandon
Jul 18, 2004
30,739
454
126
This is good advice for any hvac system. Use a super shitty filter. The "good" filter will decrease airflow to the point it effects efficiency. Bad idea.

True story. This craze of putting allergen filters in your HVAC system has caused people problems they don't even realize right away. Basic filters go in your HVAC system, and if you need separate air purification you can buy purifiers designed for that purpose.