Warm/Hot: Cyberpower 1200VA UPS - $99 @ Microcenter
I was in need of a good UPS backup for my PC's and found this deal. Not bad at all for $99.
http://www.microcenter.com/product/2...l_Connectivity
$50 less than newegg, $30 less than I've seen it elsewhere. No rebates or any other hassles. The usb and serial connectivity is great, I like that it can gracefully shut things down when power starts getting low.
|
|
|
11-06-2012, 08:30 AM
|
#2
|
|
Senior Member
Join Date: Aug 2012
Location: Closet
Posts: 823
|
I've been nothing but impressed with Cyberpower units. Much better built than APC and more software features too. Probably better still would only be a high-end Eaton unit. But man-o-man are those spendy.
|
|
|
11-06-2012, 08:54 AM
|
#3
|
|
Lifer
Join Date: Feb 2004
Posts: 20,089
|
I'm thinking of getting one for my main rig, already have one for my little server. One thing that really annoys me about UPSes are the annoying loud beeping alarm when the power goes out. On my old cyberpower there didn't seem to be any easy way to disable it, it was loud and annoying and useless, I already knew the power was out anyway....all it did was drive me nuts while I looked for a flashlight.
__________________
Error reading poptart in Drive A: Delete kids y/n?
|
|
|
11-06-2012, 09:11 AM
|
#4
|
|
Senior Member
Join Date: Aug 2012
Location: Closet
Posts: 823
|
Programmable on the new version of the PowerPanel software.
|
|
|
11-06-2012, 10:13 AM
|
#5
|
|
Diamond Member
Join Date: Jul 2005
Posts: 8,331
|
Quote:
Originally Posted by PingSpike
I'm thinking of getting one for my main rig, already have one for my little server. One thing that really annoys me about UPSes are the annoying loud beeping alarm when the power goes out. On my old cyberpower there didn't seem to be any easy way to disable it, it was loud and annoying and useless, I already knew the power was out anyway....all it did was drive me nuts while I looked for a flashlight.
|
I agree, that incessant beeping is annoying as all hell. Fortunately, there's a setting to disable that alarm now in the power panel.
|
|
|
11-06-2012, 11:44 AM
|
#6
|
|
Diamond Member
Join Date: Mar 2007
Location: B.F.E.
Posts: 3,271
|
Be aware that simulated sine wave UPSes like this one might not be compatible with active-PFC PSUs, which is why CyberPower started producing the PFC line that produces a pure sine wave.
YMMV.
__________________
"Mind your wants, 'cause there's someone that wants your mind." -George Clinton
|
|
|
11-06-2012, 11:55 AM
|
#7
|
|
Diamond Member
Join Date: Nov 2004
Posts: 7,581
|
Do any of these Cyberpower units have a low level hum or buzz while operating?
And any major difference vs. the ones with the LCD screen on them?
|
|
|
11-06-2012, 12:45 PM
|
#8
|
|
Platinum Member
Join Date: Jun 2003
Posts: 2,026
|
Thank You!
__________________
SunRey
|
|
|
11-06-2012, 02:08 PM
|
#9
|
|
Diamond Member
Join Date: Jul 2005
Posts: 8,331
|
Quote:
Originally Posted by mshan
Do any of these Cyberpower units have a low level hum or buzz while operating?
And any major difference vs. the ones with the LCD screen on them?
|
I don't know if others have a buzz or humm to them, but mine does not. It just pretty much sits there quietly.
I previously had an APC one that had an LCD on it. It's very nice/useful to be able to see the current status, wattage draw, battery status and so forth on the LCD, but I don't think it's worth paying a big premium for. You get all the same information (and a lot more) through the power panel on a PC connected to the device by USB cable.
|
|
|
11-06-2012, 02:09 PM
|
#10
|
|
Diamond Member
Join Date: Jul 2005
Posts: 8,331
|
Quote:
Originally Posted by SunRey
Thank You!
|
No problem, I've gotten lots of good deals over the years from here, glad to be able to share a good deal with others.
|
|
|
11-06-2012, 02:29 PM
|
#11
|
|
Senior Member
Join Date: Aug 2000
Posts: 583
|
I've been happy with CyberPower. One of the lower-end units, a -500 of some sort, once was completely destroyed due to a nearby lightning strike. Every peripheral connected to it was fine, every peripheral not connected to it got zapped badly. I was quite impressed by that.
|
|
|
11-06-2012, 06:42 PM
|
#12
|
|
Golden Member
Join Date: Jan 2000
Posts: 1,625
|
Quote:
Originally Posted by qliveur
Be aware that simulated sine wave UPSes like this one might not be compatible with active-PFC PSUs, which is why CyberPower started producing the PFC line that produces a pure sine wave.
YMMV.
|
For people affected by Sandy, it also won't be able to power off of a generator. I'm waiting for a good deal on the PFC line, I hope this Black Friday.
|
|
|
11-06-2012, 07:48 PM
|
#13
|
|
Diamond Member
Join Date: Mar 2007
Location: B.F.E.
Posts: 3,271
|
I got my CP1000PFCLCD for $99 a couple of years ago.
It hasn't been that cheap since.
__________________
"Mind your wants, 'cause there's someone that wants your mind." -George Clinton
|
|
|
11-06-2012, 09:04 PM
|
#14
|
|
Senior Member
Join Date: Dec 2000
Posts: 769
|
Quote:
Originally Posted by bradley
For people affected by Sandy, it also won't be able to power off of a generator. I'm waiting for a good deal on the PFC line, I hope this Black Friday.
|
Really?
I thought that the input frequency is what is important for running one of these off a generator, and if the output waveform is simulated or not only impacts if the computer powersupply would accept it. This model and the cheapest PFC model I looked at both have input frequency of 57Hz - 63Hz.
|
|
|
11-07-2012, 12:58 AM
|
#15
|
|
Diamond Member
Join Date: Jun 2005
Location: Stoughton, WI
Posts: 8,119
|
Quote:
Originally Posted by NAC
Really?
I thought that the input frequency is what is important for running one of these off a generator, and if the output waveform is simulated or not only impacts if the computer powersupply would accept it. This model and the cheapest PFC model I looked at both have input frequency of 57Hz - 63Hz.
|
Yep, It's the input frequency that matters. Most UPS's (the above included) share the same frequency handling as the output of generators (+/-5% on 60Hz). That being said, the power coming from generators is often very noisy and full of harmonics. That's why most UPS setups that are designed to run off of standby generator are the Online variety instead of Interactive variety. Portable Generators produce some of the worst power quality as far as delivery is concerned, so if this UPS is going to be interacting with a generator often, or integrated into some household Automatic Transfer system, it is worth moving to an Online unit like an Eaton hybrid / online generator or a full house online Generator (like an APC On-Line SmartUPS or Symmetra unit). An online generator separates the input and output entirely by converting the incoming AC to DC and then the DC to a pure sine wave. That way regardless of the type or quality of the power coming in, you can be certain that the power coming out is clean as can be expected.
But all being said, I suppose that's beyond this conversation. Any such units are many many times more than this unit is.
Top protect my plasma television and computer, I bought an APC SMT1500 used for $200. Its line interactive but when the power goes off (once or twice a month) the TV or computer doesn't even notice a hiccup (heck, the power in battery mode is cleaner than in standard mode because of the pure sine wave it generates off battery power.)
|
|
|
11-07-2012, 02:43 AM
|
#16
|
|
Diamond Member
Join Date: Mar 2007
Location: B.F.E.
Posts: 3,271
|
^Informative post.
The CyberPower PFC line is supposed to be able to run off of a generator, though I don't profess to know as much about this as you do.
__________________
"Mind your wants, 'cause there's someone that wants your mind." -George Clinton
|
|
|
11-07-2012, 06:27 AM
|
#17
|
|
Lifer
Join Date: Feb 2004
Posts: 20,089
|
Quote:
Originally Posted by qliveur
Be aware that simulated sine wave UPSes like this one might not be compatible with active-PFC PSUs, which is why CyberPower started producing the PFC line that produces a pure sine wave.
YMMV.
|
Hmmm, not sure if mine has this issue or not. I'm pretty sure this is the PSU I'm using:
Enchance ENP-5150GH
http://www.enhanceusa.com/file/72_specification.pdf
__________________
Error reading poptart in Drive A: Delete kids y/n?
|
|
|
11-07-2012, 06:34 AM
|
#18
|
|
Lifer
Join Date: Aug 2001
Posts: 22,235
|
Quote:
Originally Posted by PingSpike
|
That's what I have in my server, with 10 2TB HDs.
Please let me know if this UPS works for you.
__________________
Rig(s) not listed, because I change computers, like some people change their socks.
|
|
|
11-07-2012, 06:47 AM
|
#19
|
|
Golden Member
Join Date: Jan 2000
Posts: 1,625
|
Quote:
Originally Posted by thecoolnessrune
But all being said, I suppose that's beyond this conversation. Any such units are many many times more than this unit is.
|
Thanks for the information. Feel free to extrapolate. I do speak from experience however, as only my active-PFC worked off of my brother-in-law's generator during a 6-day outage, not his simulated sine-wave unit. Though there could be other factors at work here. I just hope he gives me back my unit, as he seems taken with it.
|
|
|
11-07-2012, 07:44 AM
|
#20
|
|
Diamond Member
Join Date: Feb 2002
Posts: 3,162
|
One, generators aside (never owned one), I have never had any problems running simulated wave UPS'es with active PFC power supplies, and even though the web is abuzz with warnings against it, surprisingly, there are very few (I'm almost tempted to say none) first hand accounts of simulated wave UPS'es not working with active PFC. So personally I'm convinced this is just a ploy to upsell you to more expensive pure sine UPS.
Two, isn't 1350VA model $89.99 at Costco? Although call first, availability may vary from store to store.
|
|
|
11-07-2012, 08:18 AM
|
#21
|
|
Lifer
Join Date: Aug 2000
Location: Manchester, NH
Posts: 12,557
|
Unfortunately, MC is no longer so close to me, so with shipping, it's only $5 less than Amazon.
|
|
|
11-07-2012, 08:20 AM
|
#22
|
|
Senior Member
Join Date: Sep 2000
Location: Medford, NJ
Posts: 774
|
Quote:
Originally Posted by fleshconsumed
...isn't 1350VA model $89.99 at Costco?
|
That's not listed on Costco's site, but I do recall some UPS being on their shelf and will check. I suspect that here in Sandy-landfall territory [NJ, DE, NY, CO], UPS's are no more on the shelves this week than generators are.
I've four UPS's around the house (TV[=Monitor], LAN, computer, stereo) so when we lost Power -- 5 minutes after I emailed that "Sandy" was abating and nothing hurt us -- I laughed and turned the TV back on (it always shuts-down during a UPS transition to battery)... and found my ISP (Comcast) had failed along with the Power. Sigh. [Comcast returned after 30 hrs.]
Powering LED light bulbs, the re-purposed UPS's kept lights on wherever I required them for the 40 hour outage.
__________________
Socrates is said to have advised, "By all means marry; if you get a good wife, you'll be happy. If you get a bad one, you'll become a philosopher." ... There's the question of which came first: philosophizing or being ill-tempered. Would being married to a philosopher turn a woman into a shrew?[WotD - Anu Garg]
|
|
|
11-07-2012, 08:46 AM
|
#23
|
|
Golden Member
Join Date: Jan 2000
Posts: 1,625
|
Quote:
Originally Posted by fleshconsumed
One, generators aside (never owned one), I have never had any problems running simulated wave UPS'es with active PFC power supplies, and even though the web is abuzz with warnings against it, surprisingly, there are very few (I'm almost tempted to say none) first hand accounts of simulated wave UPS'es not working with active PFC. So personally I'm convinced this is just a ploy to upsell you to more expensive pure sine UPS.
|
I've never owned anything other than a pure sine wave UPS. However you will definitely find documented cases of cheaper square wave (or step sine wave) backups wreaking havoc with active PFC power supplies, in the form of whine/buzz, instability or even making them inoperable. I'd imagine this scenario would be made more probable depening on the voltage of your linesource, whether US or Europe, and the components of the actual power supply itself.
Fluctuations wrought by square waves could also damage (over time) sensitive equipment, including capacitors. Obviously, a pure sine wave backup should measure zero distortion meaning less electrical resistance and power consumption.
Last edited by bradley; 11-07-2012 at 08:59 AM.
Reason: Add information
|
|
|
11-07-2012, 09:41 AM
|
#24
|
|
Lifer
Join Date: Feb 2004
Posts: 20,089
|
Quote:
Originally Posted by VirtualLarry
That's what I have in my server, with 10 2TB HDs.
Please let me know if this UPS works for you.
|
Well, I was more asking if it would work for me first!
Regardless, I think I'll end up passing on this. Its a good deal but with shipping its pretty expensive when my main PC can get by on something for half as much.
__________________
Error reading poptart in Drive A: Delete kids y/n?
|
|
|
11-07-2012, 10:10 AM
|
#25
|
|
Diamond Member
Join Date: Jul 2005
Posts: 8,331
|
Some very good information in this thread, thanks guys. This UPS seems to work fine with the two PC's I have hooked up to it. To test it, I just unplugged the power cord to the UPS and the two PC's kept humming along happily for at least 20 mins. I'm sure I'll do more testing, but it seems fine right now.
|
|
|